  • FIRE SAFETY

    Junaidah Jailani

  • FIRE SAFETY Principles of Fire

    Passive Fire Protection

    Building Utilization

    Compartmentation

    Means Of Escape

    Active Fire Protection

    Fire Detection System

    Fire Extinguisher

    Sprinkler System

    Mechanical Compartmentation

    Fire Safety Rules & Regulations

  • DEFINITION OF FIRE

    According to NFPA

    Fire: A rapid oxidation process with evolution of light and heat in varying intensities.

    A chemical reaction between a fuel and an oxidant.

    Any instance of destructive and uncontrolled burning, including explosion, of combustible solids, liquids, or gases.

    Any instance of destructive and uncontrolled burning, including explosion

  • DEFINITION OF FIRE

    Fire is a combustion or burning, in which substance combine chemically with oxygen from the air and typically

    give out bright light, heat and smoke.

  • PRINCIPLES OF FIRE

    To build a fire, it helps to understand the basic principles of a fire.

    Fuel (in a nongaseous state) does not burn directly. When heat applied to a fuel, it produces a gas. This gas, combined with oxygen in the air, burns.

    Understanding the concept of the fire triangle is very important in correctly constructing and maintaining a fire.

  • PRINCIPLES OF FIRE

    The three sides of the triangle represent air, heat, and fuel. If any of these removed, the fire will go out.

    The correct ratio of these components is very important for a fire to burn at its greatest capability.

  • Causes of fire:

    Short circuit

    Careless and unaware attitude among users

    Dangerous activities held in building

    Overheating

    Pipe Leakage

    Intentionally burning

    Factors contribute to fire

    Combustible materials used in building

    Combustible goods placed in building

    Poor fire fighting system in building

    * Poor space arrangement

    * Improper installation of fire fighting equipments

    Malfunction of fire fighting equipments.

    Water shortage in fire fighting system

  • CLASSES OF FIRE WHEN DECIDING ON WHAT FIRE PROTECTION IS APPROPRIATE FOR ANY GIVEN

    SITUATION, IT IS IMPORTANT TO ASSESS THE TYPES OF FIRE HAZARD THAT MAY BE

    FACED.

    Class Type of Fire Fire Fighting Agent

    A Fires that involve flammable solids such as wood, cloth,

    rubber, paper, and some types of plastics

    Water, Dry Chemical Powder,

    Foam

    B

    Fires that involve flammable liquids or liquifiable solids

    such as petrol/gasoline, oil, paint, some waxes & plastics,

    but not cooking fats or oils AND Fires that involve

    flammable gases, such as natural gas, hydrogen,

    propane, butane

    CO2, Dry Chemical Powder,

    Foam, Halon

    C

    Fires that involve any of the materials found in Class A

    and B fires, but with the introduction of an electrical

    appliances, wiring, or other electrically energized objects

    in the vicinity of the fire, with a resultant electrical shock

    risk if a conductive agent is used to control the fire

    CO2, Dry Chemical Powder,

    Halon

    D Fires that involve combustible metals, such as sodium,

    magnesium, and potassium Dry Chemical Powder

  • PASSIVE FIRE PROTECTION DEFINITION :

    - Passive fire protection (PFP) is defines as protection through ignition delays, reduce rate of burning and fire spread through use of fire-resistant walls, floors, and doors (amongst other examples).

    - It is an integral component of the three components of structural fire protection and fire safety in a building.

    ASPECTS OF PASSIVE FIRE PROTECTION:

    - Building Utilization

    - Compartmentation

    - Mean of Escape

  • BUILDING UTILIZATION

    Building utilization mean the number of persons using an undivided space, such as a meeting room, classroom, auditorium, hotel room or stadium.

    As with building codes, fire-protection authorities often set a limit on the number of people that can occupy a space.

    Reason of limitation number of person are :

    To ensure occupant must be able to leave the building through the available number of exits in a reasonable amount of time, without tripping or trampling each other In a panicked situation, possibly blinded by smoke.

  • COMPARTMENTATION Compartment means any part of a building which is separated from all other

    parts by one or more compartment walls or compartment floors or by both such walls and floors; and for the purpose of the Part, if any part of the top storey of a building is within a compartment, the compartment shall include any room space above such part of the storey. (UBBL: Part VII)

    Compartmentation is dividing spaces into small compartments which may contain single or multiple rooms.

    The purpose of compartmentation is to limit the spread of fire, smoke and flue gases

    Examples of compartmentation :

    1. dividing office area into working place, office equipments room ( photostate & paper shredder machine ) and storage area ( papers, files)

    2. dividing hospital area into treating room, operation theater and chemical storage area

  • Method of compartmentation :

    The construction of such compartments and all its components must

    focus to achieve fire resistance rating which all components are

    subject to stringent Listing and approval use and compliance in countries,

    where product certification is mandatory.

    Type of component :

    1) Fire - resistant elements

    2) Interior furnishing / ceiling

    COMPARTMENTATION

  • FIRE - RESISTANT ELEMENTS

    Firewalls are constructed of concrete or concrete blocks

  • FIRE - RESISTANT ELEMENTS Fire-resistance rated door

    This I beam has a fireproofing material sprayed

    onto it as a form of passive fire protection.

  • INTERIOR

    FURNISHING /

    CEILING

    Spraying

    fireproofing to

    the ceiling using

    a gypsum based

    plaster

  • MEANS OF ESCAPE DEFINITION :

    OSHA define an escape route or an exit route as a continuous and non-obstructed path of exit travel from any point within a workplace to a place of safety.

    An exit route consists of three parts:

    Exit access

    portion of an exit route that leads to an exit.

    Exit

    portion of an exit route that is generally separated from other areas to provide a protected way of travel to the exit discharge.

    Exit discharge

    part of the exit route that leads directly outside or to a street, walkway, refuge area, public way, or open space with access to the outside.

    emergency exit in

    Stockholm's underground

    station "Universitetet"

  • THE DESIGN & CONSTRUCTION OF THE

    EXIT ROUTES Exit routes must be permanent parts of the

    workplace.

    Exit discharges must lead directly outside These exit discharge areas must be large enough to accommodate the building occupants

    Exit stairs that continue beyond the level on which the exit discharge is located must be interrupted at that level by doors, partitions, or other effective means that clearly indicate the direction of travel leading to the exit discharge.

    Exit route doors must be unlocked from the inside. They must be free of devices or alarms that could restrict use of the exit route if the device or alarm fails.

    Side-hinged exit doors must be used to connect rooms to exit routes. These doors must swing out in the direction of exit travel if the room is to be occupied by more than 50 people or if the room is a high-hazard area.

    Exit routes must support the maximum permitted occupant load for each floor served, and the capacity of an exit route may not decrease in the direction of exit route travel to the exit discharge.

    Ceilings of exit routes must be at least 7 feet,6 inches high.

    An exit access must be at least 28 inches wide at all points. Where there is only one exit access leading to an exit or exit discharge, the width of the exit and exit discharge must be at least equal to the width of the exit access. Objects that project into the exit must not reduce its width.

  • THE REQUIREMENTS FOR EXIT Exits must be separated by fire resistant

    materials - that is, one-hour fire-resistance rating if the exit connects three or fewer stories and two-hour fire-resistance rating if the exit connects more than three floors.

    Exits are permitted to have only those openings necessary to allow access to the exit from occupied areas of the workplace or to the exit discharge. Openings must be protected by a self-closing, approved fire door that remains closed or automatically closes in an emergency.

  • MEANS OF ESCAPE

  • ACTIVE FIRE PROTECTION

  • ACTIVE FIRE PROTECTION

    Definition :

    Active fire protection (AFP) is characterized by items or system, which require a certain amount of motion and response in order to work, contrary to passive fire protection.

    There are 2 kinds of active fire protections

    1) Fire Detection

    2) Fire Suppression

  • FIRE DETECTION

    FIRE DETECTION SYSTEM

    Fire detection system is designed to identify unwanted presence of fire by monitoring environmental changes associated with combustion.

    There are 2 types of fire detection systems :

    1) manual fire detection system

    2) automatic fire detection system

    Fire detection system components consist of:

    1)Alarm

    2)Manual call point

    3)Detector (smoke, thermal / heat or flame)

  • MANUAL FIRE ALARM DETECTION

    Fire Occurrence

    Fire Detection Device

    Manual Call Point/Break Glass/ Phone

    Alarm Trigger

    Manually Call Fire Department

  • MANUAL FIRE ALARM DETECTION

    DEVICES

  • AUTOMATIC FIRE ALARM DETECTION

    Fire Occurrence

    Detected Devices (Automatic detector/Heat Detector)

    Fire Alarm Trigger

    Detected on Control Panel (Show fire location in building)

    Automatic Connected to Fire Department

  • AUTOMATIC FIRE ALARM DETECTION

    DEVICES

    Smoke Detector

    Heat Detector

    Fire Control Panel

  • FIRE SUPPRESSION Fire suppression system is used in conjunction with fire detection system to

    increase public safety. This system are governed by the codes under the NFPA (National Fire Protection Association)

    Types of fire suppression:

    1) Fire Extinguisher

    * Portable fire extinguisher

    * Automatic fire extinguisher

    2) Hydrants

    * Hose reel

    * Wet riser

    * Dry riser

    * Foam riser

    3) Smoke Extraction & Ventilation

  • FIRE EXTINGUISHER PORTABLE FIRE EXTINGUISHER

    Portable extinguishers are intended as a first line of defense to cope with fires of limited size.

    They are needed even when a facility is equipped with automatic sprinklers, standpipe and hose, or other fixed protection equipment.

    Fire extinguisher training is provided by contacting the Health and Safety Office Fire Safety Section.

  • FIRE EXTINGUISHER

    AUTOMATIC FIRE EXTINGUISHER

    1) Sprinkler system

    2) Gas / Foam system

    Fire sprinkler system

    Consisting of a water supply system, providing adequate pressure and flow rate to a water distribution piping system, onto which fire sprinkler are connected.

    There are 2 main types of fire sprinkler system:

    1) Wet pipe system

    2) Dry pipe system

  • FIRE SPRINKLER SYSTEM Wet Pipe System

    When an automatic sprinkler is exposed for a sufficient time to a temperature at or

    above the temperature rating, the heat sensitive element (glass bulb or fusible

    link) releases, allowing water to flow from that sprinkler.

    Dry Pipe System

    When one or more of the automatic sprinklers is exposed to for a sufficient time to a temperature at or above the temperature rating, it opens, allowing the air in the piping to vent from that sprinkler.

    Each sprinkler operates individually.

    As the air pressure in the piping drops, the pressure differential across the dry pipe valve changes, allowing water to enter the piping system.

    Water flow from sprinklers needed to control the fire is delayed until the air is vented from the sprinklers.

    For this reason, dry pipe systems are usually not as effective as wet pipe systems in fire control during the initial stages of the fire.

  • FIRE SPRINKLER SYSTEM

    Direct System

    In-Direct System

    Dry System: No Water in range pipe

    Wet System: Water Ready in range pipe

  • SPRINKLER SYSTEMS

    Wet Pipe Systems

    By a wide margin, wet pipe sprinkler systems are installed more often than all other types of fire sprinkler systems.

    They also are the most reliable, because they are simple, with the only operating components being the automatic sprinklers and (commonly, but not always) the automatic alarm check valve.

    An automatic water supply provides water under pressure to the system piping.

  • SPRINKLER SYSTEM-WET PIPE

  • SPRINKLER SYSTEM-WET PIPE

  • SPRINKLER SYSTEMS

    Dry Pipe Systems

    Dry pipe systems are installed in spaces in which the ambient temperature may be cold enough to freeze the water in a wet pipe system, rendering the

    system inoperable.

    Dry pipe systems are most often used in unheated buildings, in parking garages, in outside canopies attached to heated buildings (in which a wet

    pipe system would be provided), or in refrigerated coolers.

    Dry pipe systems are the second most common sprinkler system type.

    In regions using NFPA regulations, dry pipe systems cannot be installed unless the range of ambient temperatures reaches below 40F.

  • SPRINKLER SYSTEM-DRY PIPE

    Operation

    Water is not present in the piping until the system operates.

    The piping is filled with air below the water supply pressure.

    To prevent the larger water supply pressure from forcing water into the piping, the design of the dry pipe valve (a specialized type of check valve)

    results in a greater force on top of the check valve clapper by the use of a

    larger valve clapper area exposed to the piping air pressure, as compared to

    the higher water pressure but smaller clapper surface area.

  • SPRINKLER SYSTEM-DRY PIPE

    When one or more of the automatic sprinklers is exposed, for a sufficient time, to a temperature at or above the temperature rating, it opens, allowing

    the air in the piping to vent from that sprinkler. Each sprinkler operates

    individually. As the air pressure in the piping drops, the pressure differential

    across the dry pipe valve changes, allowing water to enter the piping system.

    Water flow from sprinklers, needed to control the fire, is delayed until the air

    is vented from the sprinklers. In regions using NFPA 13 regulations, the time

    it takes water to reach the hydraulically remote sprinkler from the time that

    sprinkler is activated is limited to a maximum of 60 seconds

  • SPRINKLER SYSTEM-DRY PIPE

  • SPRINKLER SYSTEM-DRY PIPE

    Disadvantages of using dry pipe fire sprinkler systems include:

    Increased complexity - Dry pipe systems require additional control equipment and air pressure supply components which increases system complexity.

    Higher installation and maintenance costs - The added complexity impacts the overall dry-pipe installation cost, and increases maintenance expenditure primarily

    due to added service labor costs.

    Lower design flexibility - Regulatory requirements limit the maximum permitted size (i.e., 750 gallons) of individual dry-pipe systems, unless additional components and

    design efforts are provided to limit the time from sprinkler activation to water

    discharge to under one minute. These limitations may increase the number of

    individual sprinkler

  • SPRINKLER SYSTEM-DRY PIPE

    Other disadvantages:

    Increased fire response time - Because the piping is empty at the time the sprinkler operates, there is an inherent time delay in delivering water to the

    sprinklers which have operated while the water travels from the riser to the

    sprinkler, partially filling the piping in the process

    Increased corrosion potential - Following operation or testing, dry-pipe sprinkler system piping is drained, but residual water collects in piping low

    spots, and moisture is also retained in the atmosphere within the piping. This

    moisture, coupled with the oxygen available in the compressed air in the

    piping, increases pipe internal wall corrosion rates, possibly eventually

    leading to leaks.

  • FIRE SPRINKLER

    Types sprinkler head : Glass bulb, Fusible link, Chemical, Open

  • GAS / FOAM SYSTEM

    Gas or foam water fire sprinkler system is a special application

    system, discharging a gas such

    as CO2 or mixture of water and

    low expansion foam

    concentrate, resulting in a foam

    spray from the sprinkler.

    These systems are usually used with special hazards

    occupancies associated with

    high challenge fires, such

    as flammable liquids, electrical

    room, computer and database

    room and airport hangars

  • HYDRANTS

    Fire hydrants consists of hose reel and riser.

    There are 3 types of riser which are:

    1) Dry Riser

    2) Wet Riser

    3) Foam Riser

  • HYDRANTS SYSTEM

    Dry riser No water in riser pipe

    Wet riser Water ready in riser pipe

  • SMOKE EXTRACTION & VENTILATION Objectives

    1) to aid fire control by eliminating smoke, heat, toxic and inflammable gasses from the source of fire

    2) to retain visibility of escapers

    3) to provide clear access for firefighters

  • FIRE SAFETY PRODUCTS/DEVICES

  • SELF TEST QUESTIONS Explain TWO (2) types of Fire Safety System in a building (10 Marks)

    Explain differences between automatic and manual fire suppression (5 Marks)

  • FIRE SAFETY RULES & REGULATIONS

    DEFINITION OF FIRE: A Reaction That Happened When A Combustible Material &

    Oxygen Is Exposed To The Source Of Heat Or Torch

    DEFINITION OF FIRE SAFETY: Action Plans By Application Of Science And

    Engineering Principals For Fire Prevention And Protection In A Particular Building And Strategies To Reduce Fire Hazards During A Fire Incident

    Protection In The Aspects Of Fire Prevention, Control & Extinguishment For A Certain Areas Based On Availability Of Risk In That Area (Jpbd:2007)

  • FIRE SAFETY RULES & REGULATIONS Fire can be extinguished by removing any one of the elements

    of the fire tetrahedron.

    Example:

    Consider a natural gas flame, such as from a stovetop burner. The fire can be extinguished by any of the following:

    turning off the gas supply, which removes the fuel source;

    covering the flame completely, which smothers the flame as the combustion both uses the available oxidizer (the oxygen in the air) and displaces it from the area around the flame with CO2;

    application of water, which removes heat from the fire faster than the fire can produce it (similarly, blowing hard on a flame will displace the heat of the currently burning gas from its fuel source, to the same end), or

    application of a retardant chemical such as Halon to the flame, which DELAYS the chemical reaction itself until the rate of combustion is too slow to maintain the chain reaction

  • Objective Of Fire Safety :

    To Identify In Details All Fixed Protection System In A Building, Both : (Passive And Active)

    Two (2) Kinds Of Fire Protections:

    1) Fire Prevention 2) Fire Protection (Active & Passive Fire Protection)

    Measures undertake to prevent the occurrence of fire : Education & Training

    Enforcement

    Engineering

    Security

    Maintenance

    Good Housekeeping

    FIRE SAFETY RULES & REGULATIONS

  • 1) Uniform Building By Law (UBBL) 1984,

    - Part VII-Fire Requirements

    - Part VIII-Fire Alarms, Fire Detection, Fire Extinguishment and Fire Fighting Access

    2) National Fire Protection Associations (NFNA)

    3) Law by Fire Department (Akta Perkhidmatan Bomba 1988)

    LAWS & REQUIREMENT ON FIRE SAFETY

  • 1) Uniform Building By Law (UBBL) 1984

    ~ UBBL, is a published document, which is used as a required safety standard and is emphasized by government.

    ~ The FRDM strive to discharge its responsibilities in its prevention & safety program, and also its enforcement in relation to inspections of buildings & business licensing activities according to UBBL especially Part 7 & Part 8

    Part 7 : Fire Requirement

    Part 8 : Fire Alarm, Fire Detection, Fire Extinguishment & Fire Fighting Access.

    LAWS & REQUIREMENT ON FIRE SAFETY

  • One of a crucial stage in building design

    Building plans required to be approved by the Fire Department (Jabatan Bomba & Penyelamat Malaysia- JBPM) before the building can be constructed.

    Once the construction finished; the building itself will again required to be inspected before approved by JBPM.

    The practice is part of the requirements by the Local Council before CF is issued.

  • GOOD BUILDING DESIGN WITH FIRE SAFETY MEASURE Provide adequate fire appliances, fire hydrants and other facilities to

    assist fire and rescue personnel

    Provide adequate fixed installation where appropriate, for quick & effective detection & extinguishment of fire

    Designing & installing building services so that they do not assist the spread of fire, smoke or any toxic fumes.

    Designing & providing adequate & safe escape route for the occupants of the building

    Selecting materials for the construction which will not promote the spread of fire or generates hazardous smokes.

    Subdividing building into compartments of reasonable sizes by mean of fire resisting floor& wall, providing fire stop to protect openings between floor & compartments

    Designing & constructing the exterior of a building so that the fire unlikely to spread to it from another burning building