Zero Sequence Filters For Harmonic Mitigation Tyrone Ding, Pooya Bagheri [email protected], [email protected] The proliferation of the energy-efficient consumer electronic appliances in modern households has resulted in significant voltage and current waveform distortions in residential distribution systems. Although each of the consumer electronic appliance is not individually a big source of harmonics, the collective effect will be considerable and can become a serious concern of utility companies. Due to the fact that most of residential loads are single-phase, Zero- Sequence (ZS) harmonics are expected to be created at the three phase distribution feeders feeding them. High levels of ZS harmonics could lead to neutral voltage/current raise and interference problems with the adjacent telephone lines. Therefore, the ZS harmonics must be considered when researching the harmonic mitigation solutions for modern residential feeders. Introduction Traditional ZS Filters Power and Energy Innovation Forum ♦ University of Alberta ♦ November 2013 Zero Sequence Frequency Scan of Designed Filters A B C A B C A B C (a) Star-type (b) Star-type including a three-phase inductor (c) Zig-zag transformer-based The main drawbacks of traditional ZS filters are: • The star-type (a) and (b) can affect the fundamental power flow and may lead to positive or negative sequence resonances at other frequencies. • The zig-zag transformer-based type needs a nonstandard transformer. Transformer-based ZS Filters Here the transformer-based ZS filters is developed from the concept of grounding transformer. Such filters behave as an open circuit at positive and negative sequences so it has no impact on normal power system operation and non-zero-sequence harmonics. C A B C N A B C N (a) Single-tuned Expanding the filter configuration to trap two harmonic orders with just one transformer (b) Double-tuned Expanding the filter configuration to trap three harmonic orders with just one transformer A B C N (c) Three-tuned C 3 L 1 C 1 C 2 L 2 C 2 L 2 C 1 Telephone Interference Mitigation Case Study The 240/25 kV Substation Downstream loads Upstream loads Filter Location Telephone line sections Monitoring Location F Transformer Size 75 kVA Single-tuned version C 10.29kVar Double-tuned version C 1 7.00kVar C 2 24.60kVar L 2 40.60μH Three-tuned version C 1 16.46kVar C 2 11.57kVar C 3 10.29kVar L 1 206.35μH L 2 293.35μH 3rd 5th 7th 9th 11th 13th 15th 0 2 4 6 8 IDD(%) Simulation Results No Filter Single-tuned filter Double-tuned filter Three-tuned filter The single-tuned filter is tuned to filter 9 th harmonic, double-tuned filter is tuned to filter 9 th and 15 th harmonics and three-tuned filter is tuned to filter 3 rd , 9 th and 15 th harmonics. 0 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 0 1000 2000 3000 4000 5000 Harmonic Order Zero Sequence Impedance ( ) Single-tuned Double-tuned Three-tuned Key Design Procedures Substation A block of residential loads (e.g. a neighbourhood) Filter Normal Harmonic flow New harmonic flows after the filter is installed • Determine ZS filter installation location. • Assess transformer loading level. Both of these two key design procedures are based on the harmonic flow study of the problematic feeder.